ge fanuc run led

basharath

Member
Join Date
Mar 2010
Location
hyderabad
Posts
103
dear all
the plant has started after a long time and the gefanuc 28pt micro plc is not showing run led.
what can be the problems and how to solve them.
 
It is most likely that this unit has been installed without a battery on the RAM, or the battery is dead. If you are lucky the program will be available in backup form on the installed CPU's Flash memory or in the files on a CD or USB drive.
 
dear russ u r 100% r8,yesterday i went to site and found there was no logic in the plc...thanks i have kept its backup with me....

what i thought was might be some outputs are not working...but it was as u said..this is where the experience works.
 

Similar Topics

Dear Everyone I work with PLC GE-Fanuc. But I don't know that "PLC GE-Fanuc (Series 90-30 and VersaMax) can Online Edit Programming while...
Replies
9
Views
3,092
We have a GE Fanuc PLC 90-30. After power cycle, it would not go into run mode. Power LED on, but no Run LED. No Fault LED either. When we got...
Replies
2
Views
2,509
Good morning, I have a R30iA Fanuc Controller with a main routine running 24/7. Recently, we have added a new machine to the cell, so this...
Replies
8
Views
5,619
Hi I've got a GE Fanuc 90-30 that had a faulty output card. I powered down, then replaced the card and powered up. The PLC won't go back into...
Replies
30
Views
31,885
Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
Replies
0
Views
51
Back
Top Bottom