GE PLC VersaMax ic200udr140 problem

morty

Member
Join Date
Feb 2017
Location
taiwan
Posts
8
i have problem about GE PLC VersaMax ic200udr140

It has been set to ip connection
But i do not know ip
How i want to initialize it?
 
Page 338 of GFK-1645L shows the pinout of DB9 to rj-45 RS-232 you could use a cable . Or could try using program Advanced IP Scanner and use crossover Ethernet or a switch and scan and get the ip address of the device.. just have computer and udr140 connected when polling.
 