Hello Team,
I am working on a project utilizing the new implicit communication with the 208-L50E-***** (specifically a 28QWB). this is a two part question.
1) the Third Party Device I am working with is set up with a Data Type of SINT with a 20.0ms RPI and the following communication configuration
1. Instance 100, Size 210 (Input, Producing Data)
2. Instance 105, Size 190 (Configuration)
3. Instance 150, Size 210 (Output, Consuming Data)
after I have named and created the Generic device I then need to load the information into the configuration table. The Manual is showing Hexadecimal values and when I convert them to decimal for the CCW variable table some of them exceed the range of the SINT data type (-128 to 127)
MIO_67_TPRegrip_C[0] : 0x01 hexadecimal (number of modules)
MIO_67_TPRegrip_C[1]: 0x00 hexadecimal (always 00)
MIO_67_TPRegrip_C[2]: 0x91 hexadecimal ( Digital I/O module start)
MIO_67_TPRegrip_C[3]: 0x01 hexadecimal
MIO_67_TPRegrip_C[4]: 0x03 hexadecimal
MIO_67_TPRegrip_C[5]: 0x80 hexadecimal ( Digital I/O module stop)
And the rest should be 0x00 since I have no other modules
has anyone experienced a similar issue is the workaround possibly as simpble as changing it to a DINT data type and using more memory?
Secondly, we have set up a 1734-AENT as a generic device as well we have got it communicating and recognized as running inside of CCW with out the ability to check a box to change the default setting of Load checking on the 1734-OB8E where all the outputs lights are flashing until a load is wired does anyone know which bit in the confuration table will shut that off?
I am working on a project utilizing the new implicit communication with the 208-L50E-***** (specifically a 28QWB). this is a two part question.
1) the Third Party Device I am working with is set up with a Data Type of SINT with a 20.0ms RPI and the following communication configuration
1. Instance 100, Size 210 (Input, Producing Data)
2. Instance 105, Size 190 (Configuration)
3. Instance 150, Size 210 (Output, Consuming Data)
after I have named and created the Generic device I then need to load the information into the configuration table. The Manual is showing Hexadecimal values and when I convert them to decimal for the CCW variable table some of them exceed the range of the SINT data type (-128 to 127)
MIO_67_TPRegrip_C[0] : 0x01 hexadecimal (number of modules)
MIO_67_TPRegrip_C[1]: 0x00 hexadecimal (always 00)
MIO_67_TPRegrip_C[2]: 0x91 hexadecimal ( Digital I/O module start)
MIO_67_TPRegrip_C[3]: 0x01 hexadecimal
MIO_67_TPRegrip_C[4]: 0x03 hexadecimal
MIO_67_TPRegrip_C[5]: 0x80 hexadecimal ( Digital I/O module stop)
And the rest should be 0x00 since I have no other modules
has anyone experienced a similar issue is the workaround possibly as simpble as changing it to a DINT data type and using more memory?
Secondly, we have set up a 1734-AENT as a generic device as well we have got it communicating and recognized as running inside of CCW with out the ability to check a box to change the default setting of Load checking on the 1734-OB8E where all the outputs lights are flashing until a load is wired does anyone know which bit in the confuration table will shut that off?