going online to compact logix via enbt
stallone
Oct 2010
south africa
172
Hi all,
i have a plc rack with control logix 1756-L61 (rev 12) and in the rack is the plc, controlnet card 1756-cnb/d, and the 1756-enet card.
I can go online via a rs232 cable to the plc directly.
I cannot however go online via the ethernet port of the enet card in the rack.
I am in the same ip range as i can ping and get a reply from the card but rslinx cant browse the enet card and i cant browse it in rswho.
I have my scada connected to the plc rs232 port and i would like to leave it connected and at the same time go online to the plc via the ethernet port, therefore i can see scada indication and plc bits same time.
Is there any trick to the above:)
Verify that the part number is 1756-ENET. These were the original 10 MB half-duplex Ethernet modules for ControlLogix.
To verify that you are using the IP address, I recommend trying to connect to the 1756-ENET using a Web browser, or by using TCPING (from elifulkerson.com) with TCP Port 44818.
You can also browse across the backplane from the CPU's RS-232 port and right-click on the module to see its configuration.
There are two RSLinx Ethernet drivers; the "Ethernet Devices" and the "EtherNet/IP" driver.
You will need to use the Ethernet Devices driver, in which you must add the IP address of the 1756-ENET to the station list.
I think that the old 1756-ENET modules did not support the broadcast packet type of browsing that the modern EtherNet/IP driver uses, so they would not show up in that driver.
it is definatly the 1756-enet/A.
i can ping the enet card using cmd/run cammand in windows.
when i am online with the rs232 port on the plc i can see the enet card and it is working and no faults. the ip address i see is the ip address im using.
i must say i have been trying to use the ethernet/ip drivers.
Just an update, i went and setup the Ethernet devices driver and set the ip address as the host name and connected straight away.
Thank you Ken Roach:)
Hello there...I was wondering if someone can help me out. I am a co op student in the controls dep in a manufacturing facility and have some...
4,548
I do have a problem with a GE Versamax micro PLC. By going online (on Port 1) the "OK led" goes down. Power led stays On Port 2 no reaction at...
396
Good Afternoon. I am having a problem going online with S7-400. Attached is the error that I am getting. I have looked at the help file but the...
1,785
The machine is running production. When trying to go online with the laptop the whole machine looses communication and faults out. Drives, HMI...
1,946
Hi I have a machine that has 1500 cpu program is v15:1 I have the program from the Oem and the tia portal software v15.1 ? I have set the laptop...
1,879