Good Program Design for an OR Branch With Latching?
TL140
Jun 2014
South Carolina
152
I was reading Programmable Logic Controllers: An Emphasis on Design and Application, By Kelvin T. Erickson (great book, highly recommend) and I remember that there was a section saying that the following situation was bad programming practice, but I cannot remember the solution. I wont have my book back for a few weeks and I thought that you guys may also have your own approaches so I figured why not ask you guys.
Situation:
Basic On/Off motor w/ memory with also an HMI start button. Logic would look a lil like this..
Start Stop M1
HMI_Start |
M1 |
What would you guys use?
I'd start the rung with the STOP contact, then have the seal in branch.
In some PLC's it makes no difference, as they will scan everything in every rung anyway, but in others, as soon as a false condition is detected, the rung evaluation stops and the output(s) are updated.
There is absolutely nothing wrong with this approach.
I would like to know the arguments as to why it is bad programming style.
As long as the rung doesnt become very huge, it is more easy to understand in a hurry, as opposed to splitting into separate -(S) and -(R) rungs.
The HMI_start is dubious though.
There is no HMI_stop, so is it a toggle switch or a momentary button ?
If a toggle switch, if HMI_start is true, M1 will stop and then restart when Stop is pressed.
If it is a momentary button, there is the risk that the state hangs if the HMI is shutdown or there are comms problems. I prefer to generate oneshots for momentary HMI buttons, and then use the oneshot states for the start/stop logic.
The only thing I do differently from the "bad" example would be to add check's for: (as appropriate)
Motor OverLoad Relay, Tank Level OK (if a pump), Lid or Safety Open, MCR On, E-Stop ON, etc between the STOP and M1 Output. That way the output will be shut off if any of the safety items trip. Otherwise I use exactly that line many times.
The logic can be improved if you use a confirmation signal from the output device instead of the command as the sealing contact. For example, if M1 is a motor starter, wire an auxiliary contact from the starter to a PLC input and use the aux contact in place of the M1contact. That way, if the starter trips out on an overload, the PLC will also turn off the command to the starter.
If one uses oneshots on HMI buttons (as I suggested earlier), you cannot use the aux contact for seal-in.
Btw, we also use oneshots on hardware start-buttons. If it is stuck on, the motor wont start. No oneshot on the hardware stop-button.
As to that the contactor drops out or does not engage, there should be alarms that monitors this, and the alarms should be in series (negated) with the stop button.
HMI buttons can be tricky. They can get stuck in the on state. Hence the practice of using one-shots.
You can turn an HMI button into a one-shot by the following code inserted at the end of the PLC's main routine.
HMI_Start HMI_Start
----] [-----------------------------------(R)-
That doesn't work around the issue of having to wait for the feedback signal before turning off the HMI button. For that you can use the following:
HMI_Start Feedback HMI_Start
----] [------------] [-------------------(R)-
HMI_Start HMI_Start
I program my HMI buttons as Momentary, but I always have logic in my PLC or Controller that looks at the point that the HMI is controlling and if it is ON for a period of time (say 2 seconds), it gets turned OFF by the PLC or controller.
Admittedly, I typically use Redlion HMIs and Honeywell HC900 controllers and they make this programming simple, but I use this method when I program PLCs too.
I also *always* program a popup to actually make the change. The actual pushbutton will be on the popup. It becomes a sort of "Are You Sure?" without actually asking the question.
thanks for the input guys. Once I get the book back, I'll be sure to update on what was written. Shoot, I may even be thinking of something totally different haha. But nevertheless, I have learned some things in this thread.
Well it was more of a quick write up. It may have had a HMI stop, but I wanted to more or less demonstrate on the OR input with the latch as well. Like I said in my previous post, I may have though of something totally different.
I agree with with one shots on hard wired pushbuttons. I had a line awhile back that would start up on its own because of that reason. As far as the rung goes I set mine up like that. But as stated by others stop pb go on the left side then start on and seal in then the condition inputs motor overload, safeties ok etc then the output
When I program things, I put the most common on item in the main line & branch down in order to the least common on item. When I check conditions that must be met I start with the least common on item & progress to the most common on item.
Maybe the example is "bad" because the Start PB is on the main line, which would be the least common on item & forcing the CPU to process the branches almost every scan.
The attached picture is how I would order the rung to improve scan time.
I’m currently starting a brand new design with a compactLogix controller and a panel view 700. I’ve completed similar projects from start to...
1,242
Hello, I have been a electrical/PLC tech for about 10 years. I am now looking into get into design instead of just troubleshooting. I...
3,615
Evening all... I have got to the stage at work where I am taking on more code writing then, fault finding. My problem is, my current approach is...
2,488
For those of you on your own - how are you estimating hours on program design? I've heard of people basing it on the I/O count but that doesn't...
3,022
Do anyone know if there exist standards for PLC program design. For example if I want to design a program to control water flow into a tank, are...
5,188