Hall effect sensor wiring question
1024alexjones
Apr 2017
Alabama
Which model do you have?
Operating Supply Voltage (MP101401) 4.5 to 18 VDC
Operating Supply Voltage (MP101402) 4.5 to 24 VDC
If it's the second one I would use a relay with a coil that has a resistance >1.2k (24v÷20mA).
Without a pull up resistor,the coil will be connected to Vcc and Out with flyback diode
you will need a 3k resistor as recomended, so the current will be around 7 mA.
This is good enough for a PLC, however most PLC will work on 24 Volt and that is too high for the sensor, and a simple relais will also not work as the current is way higher as 10 mA.
Unless I am missing something here, if you are using a pull-up resistor, you will be able to connect it directly to the PNP PLC input, only your logic will be opposite (input on when the sensor is off and vice versa).
The sensor output is an NPN transistor so this is a common method of a quick conversion.
Have you tried measuring the output with just a meter and no relay hooked up?
How do you have your relay connected?
EDIT
+1 LadderLogic, I was also thinking about that.
I am trying to use this (http://www.mouser.com/ds/2/833/Magnetic-Proximity-Sensor-MP1014-Datasheet-1075726.pdf) sensor to detect a weak magnet and to switch a relay (24vdc) so that I can switch a PNP input on a PLC input card. I have tried using the pull up resistor as the document suggests but I am getting nowhere and now im afraid that I have burned the sensor up somehow. How would you set this thing up?o_Oo_Oo_O
It's not that hard if you're familiar with electronics.
You connect the 24V relay between Vcc (24V) and output on the hall effect sensor. And that is it. No resistors.
Then you wire 24V to the relay contacts to feed the 24V input on the PLC when the coil is energized.
Relay coil has to be less than 20mA.
It's not the best way to solves this though.
Best way is to pick an industrial hall effect sensor, like http://www.baumer.com/de-en/products/presence-detection/magnetic-sensors/hall-sensors/
Second best way is to use a NPN to PNP converter instead of a relay. Like http://uk.rs-online.com/web/p/signal-conditioning/5329980/
A third option is to buy a NPN input module for the PLC.
It is possible to connect a NPN output to a PLC input designed for NPN outputs, but the resistor you need depends very much on exactly what design the PLC input is and how much impedance it has. It's the last resort option, not recommended.
Hey guys, I am building a small prototype for a Coolant Dispensing System and need to measure the flow rate of water & chemical in the pipe in...
3,656
Good day, Has anyone had experience with using hall effect sensors? I know that they work on changes in a magnetic field to produce and output...
2,624
Hello guys, I need some help. I read all the old posts on hall effect sensors but none dealt with my module. The system uses a Gemco 194761 RFO...
1,723
Hi all, I have an issue with a hall effect flow meter. It is connected to a ML1100 PLC, using a High Speed Counter. Since the unit is open...
4,056
Hi all. This thread and many more before that mentions the differences for support polices for various PLC brands. Some brands provide free...
24
6,456