Hart Network wiring
Steve_D
Jul 2002
Albury/Wodonga
92
Hi guys, I am about to purchase a Hart to modbus converter to interrogate a few flow meters on hart and get the info via modbus. All looks good except the wiring diagram for the HART PART is very simplistic, i.e the converter at the start and a single line across the line of flow meters with a single line down to each meter. This is clearly 2 wires (+ and -) but I assume they are daisy chained, i.e. the 2 wires out of one become the two wires into the next. Am I right or can I bring two wire into a terminal strip and parallel the signal wires off these?
Thanks in advance
It depends on what you're doing with the HART 4-20mA output from each of the flow meters.
1) If you need a process variable data value (like flow rate) from each of the flow meters, then you need a separate HART-Modbus converter for each flow meter.
The 4-20mA runs in series through the HART-Modbus converter, AI, power supply and back to the flow meter (order does not matter).
The AI gets a modulating 4-20mA, the converter gets the total value.
2) If you need only the total from the flow meter, then the device uses Multi-drop mode - one HART-Modbus converter is needed which can poll and get data from multiple field devices.
The 4-20mA is wired in parallel to HART-Modbus converter.
Thanks DANW..its the second one, I thought as much but its comforting to get a second opinion (and by way of no one correcting you a third,fourth and onwards opinion)
I am doing a bit of research before the next project hits. For what I am finding to looks like you *should* be able to set up a multidrop HART...
3,812
I would like to install a non HART device in a system that uses HART, do you have a converter
106
I am going to need to use HART multi-drop in order to handle a series of Vega Radar units. There are a lot of options and I'm wondering what...
271
I'm not actually in front of the equipment yet, but this is the information that I have been given by a client: ------------ Data from HART...
344
Just started working with some HART loops and I'm trying out Pactware.I'm using Krohne and it works just fine recognizing my modem. I downloaded...
1,416