Heidenhain Linear Encoder with CompactLogix
cstech
May 2011
TN
34
I have the choice between a TTL pulse train and 1 Vpp versions - which would be easier to integrate with the AB 1769? I know there is a 5V TTL input card...
Thanks!
Chip
Any input here?
I have done some additional research, and found that AB makes a 1769-IG16 module that takes a TTL input. Is this the preferred way to integrate a linear encoder like the Heidenhain? I have very limited experience integrating encoders with PLCs, so this is new territory for me.
Heidenhain also makes the 1Vpp output version, but I am not sure what type of input module to use with that.
Thanks for the help!
Chip
TTL.
The AC version (1Vpp) is a "raw" signal, only for those (OEM's) that want to design their own conditioning electronics.
Use a high speed input specified for encoders.
You don't want to use a TTL input module as the scan will not be fast enough to pick up the encoder transitions. You want to use a 1769-VHSC and a TTL output encoder.
Keith
Thanks to both of you - that is exactly what I was looking for!
I already have a 1769-HSC card in the system for getting RPM from a spindle sensor, so it's good to know I can use that for both things. Anything I should be on the lookout for with wiring the TTL encoder output to the 1769-HSC?
Thanks again!
Chip
Not that I can hink of. The inputs are differential so make sure you have either a differential output or you bring a common from the encoder over.
Keith
Okay, I have successfully integrated the TTL signal encoder into the 1769-HSC, and am getting counts in the register. That's the good part.
How can I use one of the other counters for a proximity sensor (spindle RPM)? All of the HSC card setups I have tried yielded card faults.
If it helps, the current setup I am using is 1 counter in Encoder X1 mode. The AB manual doesn't specify how to "mix & match" encoder and discrete inputs.
Ideas?
hi all, i have an ls 503 heidenhain linear encoder, used to measure the axis movement length, the encoder reads the motion length of the axe, the...
3,424
Hi What are the rules for choosing a heidenhain EnDat encoder? I have a broken encoder on my Baumuller servo motor need to be replaced...
1,396
Dear Members: I am new in Beckhoff Twincat system. I am working on a project. I am using CX9020 as my embedded PC. I have connected EL5101 as...
6,182
2,121
Hello, My friend has a machine with Heidenhain 355 and when he tries to start it, he gets Error 83. I found description of this error: 83 PLC...
4,472