Help please,.temperature sensor outputs show 999.9....
DavidNelly
Jan 2008
JURONG
Dear colleagues,
I am very new to industrial and now I am trying to fix the plastic injection machine. On terminal display, 5 sensors outputs show 999.9 and machine can not start. I changed the sensors, but the result is the same. Only changing to 888.8. wiring from sensors to control board is checked and ok. Any idea ? please.
regards,
PLC brand and input module part # would be helpful, but if I had to take a stab at it, you could have lost DC power to your input board and so everything is defaulting to possibly a failsafe high temp condition. Or they are reading negative and the scaling on your display clamps to max value expecting an unsigned integer, again due to loss of DC power. A signed integer value -1 for example, reads 65535 as unsigned.
Dear robertmee,
Yes, there is a negative voltage regulator ic( 7905 )and it was not working properly. So, I change it and now the display shows 760.00. The positive voltage regulator is ok. output 4.99V.
The controller is A62B. There are 3 i.o ports. I can not get it manual.
Hello everyone, We have an application in TIA Portal (with ET200SP) to manage the furnace temperature control according to an operator setpoint...
6,118
please help me . I have to make this ladder diagram and I can’t figure it out :(
413
82
Hello, I am trying to get a Yokogawa Hart pressure Transmitter and a Rosemount Temp Transmitter to read on a 1769-IF4 module on an L33ERM...
399
Please help me, I have solve many week but still not solve it. I found trouble of factory talk studio when I set tag by browse address of OPC...
132