Help to create ESD signal

shazad5444

Lifetime Supporting Member
Join Date
Feb 2014
Location
Houston
Posts
126
PLC Guroos,

I need to configure an flow switch ESD signals, but all relevant instruments are in another PLC system, both PLC's are connected with each other through Ethernet. Can I use Produced/ Consumed or message instruction to generate ESD signal? I mean in between PCS and SIS PLC panels?
__________________
Shah
 
Does your industry allow general-purpose programmable controller devices and networks to be used in Safety-Instrumented Shutdown systems ?

Are any of these systems using GuardLogix, or any of the high-availability technologies from Rockwell like SIL2 I/O or Redundancy ? You mentioned "Produced/Consumed Tags", which is a phrase associated with Rockwell's ControlLogix family controllers.

I don't have a lot of experience with SIS systems in petrochemical applications, but if somebody told me they wanted to use sensors from a different control system in their SIS, my instinct would be to tell them no.

What sort of sensors are you using ? What sort of controllers ? What sort of I/O modules ?

And what safety standards apply to your application ?
 
Ken, It is Gas compression plant, I need to configure Flow switch as ESD signal on client request, to configure flow switch I need to add some other signals too, as in plant start up time there is no flow, I'm thinking to take flow transmitter signal, This flow transmitter is also installed on the same line but its signal is coming to PCS, so I want to use produced / consume take it to SIS PLC and configure with flow switch. We have Control Logix 5571, No we don't have Guard Logix or retendency in our System, Our SIS PLC system is only for shutdown signals, all other signals and alarms are coming to PCS PLC system, Both PLC are communication with each other through Ethernet.
 
The most important thing I learned when I took my Professional Engineer's exam was to recognize when I'm out of my area of expertise. I do discrete manufacturing systems, not oil and gas process control.

I don't know what sort of standards and requirements a gas compression plant needs for its safety shutdown system. I've worked beside a few, close enough to feel the heat from the flares, but never on the control systems inside.

But I'm pretty confident that an emergency shutdown system for a gas compression plant needs more than a general purpose logic controller and a non-redundant networked flow transmitter.

If I were in your shoes, I would appeal to a level of the company or consultants who are familiar with the process, the standards, and the risk analysis, in addition to the technology used in the programmable controllers.
 

Similar Topics

Hi, I'm having trouble understanding my course and I need help please. Can someone please write a program for this process? I will use the answer...
Replies
24
Views
6,370
Im trying to create a save button that will allow the data once inserted in the form, save to a notepad file. The file can be accessed later for...
Replies
5
Views
1,586
Hello, I've been trying to create a "duplicate" of de points in the group I "demo_point" so I've created a copy of the script but Ichanged the...
Replies
1
Views
2,280
Hi friends, i need a help to know the procedure and steps to connect Lenze i700 to PC for parameterize. i tried with lenze easy-starter using LAN...
Replies
0
Views
1
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
7
Views
221
Back
Top Bottom