Aazim Raza
Member
Hey all,
I am having an issue concerning the Modicon System Responsible for the operation of our Generator System. (Particularly Dresser-Rand SFGLD 560).
The Problem is with the analog Output Module BMXAMO0410, which unexpectedly Malfunctions and trips the Generators. (one Channel of this module is responsible for Maintaining and controlling Voltage via AvR).
The output of All 4 channels in the module stops and only 1 green status Led is stable on the Module.
Then we have to Power Recycle the Rack to normalize the module. Although, the problem again arises after almost every other week.
We also replaced the Analog Output Module, and the problem vanished. But after 3 to 4 months of operation, the same issue was raised again and we are clueless.
We also accessed the debug option from Unity Pro for the module and it stated as
External fault - Power Supply Fault
Internal Fault - Module Unserviceable
Other Fault - Application Fault
After power recycling, these faults gets reset.
Can anyone help me with the problem??
I am having an issue concerning the Modicon System Responsible for the operation of our Generator System. (Particularly Dresser-Rand SFGLD 560).
The Problem is with the analog Output Module BMXAMO0410, which unexpectedly Malfunctions and trips the Generators. (one Channel of this module is responsible for Maintaining and controlling Voltage via AvR).
The output of All 4 channels in the module stops and only 1 green status Led is stable on the Module.
Then we have to Power Recycle the Rack to normalize the module. Although, the problem again arises after almost every other week.
We also replaced the Analog Output Module, and the problem vanished. But after 3 to 4 months of operation, the same issue was raised again and we are clueless.
We also accessed the debug option from Unity Pro for the module and it stated as
External fault - Power Supply Fault
Internal Fault - Module Unserviceable
Other Fault - Application Fault
After power recycling, these faults gets reset.
Can anyone help me with the problem??