I';m hoping someone can help me with this one...
Yesterday, one of two Powerflex drives wouldnt power up. We changed the drive, but re-used the Devicenet adapter (Node1). Drives fires up fine without adapter installed, but faults on error F071 (Net Loss) when it's attached.
If I take the same Devicenet adapter, change the DIP switch settings to node 2 (the same address as the drive that didn't burn out) and install it on the other drive, it works fine. So, I know the adapter is OK.
Parameters that affect comms (A103 - A107) are identical to the partner drive. P036 = 5, P038 = 5)
Anny suggestions?