I';m hoping someone can help me with this one...

Yesterday, one of two Powerflex drives wouldnt power up. We changed the drive, but re-used the Devicenet adapter (Node1). Drives fires up fine without adapter installed, but faults on error F071 (Net Loss) when it's attached.

If I take the same Devicenet adapter, change the DIP switch settings to node 2 (the same address as the drive that didn't burn out) and install it on the other drive, it works fine. So, I know the adapter is OK.

Parameters that affect comms (A103 - A107) are identical to the partner drive. P036 = 5, P038 = 5)

Anny suggestions?
 
I';m hoping someone can help me with this one...

Yesterday, one of two Powerflex drives wouldnt power up. We changed the drive, but re-used the Devicenet adapter (Node1). Drives fires up fine without adapter installed, but faults on error F071 (Net Loss) when it's attached.

If I take the same Devicenet adapter, change the DIP switch settings to node 2 (the same address as the drive that didn't burn out) and install it on the other drive, it works fine. So, I know the adapter is OK.

Parameters that affect comms (A103 - A107) are identical to the partner drive. P036 = 5, P038 = 5)

Anny suggestions?

Is it possible you have a bad/damaged cable connecting the 22-COMM-D to the first PF40?

Stu....
 
Is it possible you have a bad/damaged cable connecting the 22-COMM-D to the first PF40?

Stu....

Cable is OK.

There is one PLC (CompactLogix) and three nodes on the network. Node 1 was the drive that failed. nodfe 2 is the sister drive and node 3 is a Festo pneumatic valve bank. Node 2 & 3 are OK.

When I take the 22-COMM-D off node 1, reconfigure the DIP switches to node 2 and re-apply power, it works. If I reconfigure the 22-COMM-D from node 2 to node 1, it won't work.

I tried moving the Pheonix connectors around with no improvement.
 
Cable is OK.

There is one PLC (CompactLogix) and three nodes on the network. Node 1 was the drive that failed. nodfe 2 is the sister drive and node 3 is a Festo pneumatic valve bank. Node 2 & 3 are OK.

When I take the 22-COMM-D off node 1, reconfigure the DIP switches to node 2 and re-apply power, it works. If I reconfigure the 22-COMM-D from node 2 to node 1, it won't work.

I tried moving the Pheonix connectors around with no improvement.

I would take the Problem PF40 out of the DeviceNet Scan List, note its I/O Location first, and then put it back in in the Scan List, and remap the its I/O. I have had to do this before because of slight differences between the old VFD and the new one. However, I can't remember if the Communications problems were on the Drive side or the DeviceNet side.

Stu....
 
I would take the Problem PF40 out of the DeviceNet Scan List, note its I/O Location first, and then put it back in in the Scan List, and remap the its I/O. I have had to do this before because of slight differences between the old VFD and the new one. However, I can't remember if the Communications problems were on the Drive side or the DeviceNet side.

Stu....

Thanks. This never occurred to me, but it's worth a try. I'll be surprised if it helps, though, because the drive is reporting the Net Loss error.
 
Thanks. This never occurred to me, but it's worth a try. I'll be surprised if it helps, though, because the drive is reporting the Net Loss error.

I agree, it might not help, but I think it is still worth trying. Yes, it is a very strange error in this situation. I suppose it is possible there is a problem with the new VFD, but it seems unlikely. The Troubleshooting information for that Error in the PF40 Manual is pretty obvious, and I am sure you have looked at those. I don't recall ever having that Error on any of the PF40s I have worked on.

Do you have another PF40 to try and eliminate the VFD itself?

Stu....
 
Solved!

We had to remove node 1 from the Devicenet schedule the re-schedule it.

I thought this would have been a simple change-out, but Allen-Bradley hardware always seems to have something quirky that you have to contend with.

Thanks for the help, guys!
 

Similar Topics

Hi Guys, I'm taking a night school course and its a project course . I'm using control logix v15 and a power flex 40 drive . I have to program...
Replies
7
Views
5,707
Hi Just wondering has anyone had anything like this happen to them? I have just split a safety cct which previously used a single safety relay...
Replies
14
Views
12,450
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
2
Views
267
Hi all, I am having a problem with a powerflex 753 we have on site and keep getting input phase loss. The drive has been running for a long...
Replies
7
Views
1,388
After replacing the 70 with the 525, the PLC can read from the drive and recognizes it as online, but no commands are being listened to. PLC is...
Replies
1
Views
584
Back
Top Bottom