Help with problem please. This is an omron plc (CP1L) cx programmer.

Tony chacon

Member
Join Date
Sep 2013
Location
Winnipeg
Posts
1
In the hand position:
Pumps 1 and 2 are controlled and alternated by the hand selector switch. When Hand position is first selected, pump 1 will run, then turn off when OFF position is selected. The next time the hand position is selected, pump 2 will start and run until OFF position is selected. The pumps will alternate in this fashion. Only one pump is to be on at one time.
 
Welcome to the site
This is normally a student question.
There are heaps of posts so please search the site.
look at the Keep function help
also consider the counter function.
as far as using a HAND selector with alternative pump use.
this would be very bad practice as you may be wanting to test that pump.
normally C/O is in AUTO only
 
If you use greather then function block you can switch between the different pumps, we did this in school a year ago and it worked very good, only problem is when one of the pumps crashes...
then it will not work.
 

Similar Topics

we have siemens pc677 touch screen running iconics program opc and others from german beverage khs machinery .. also we have siemens plc 400...
Replies
0
Views
1,804
Hi guys, i just got my hands on a siemens s7-200 226 cpu (code 6ES7 216-2AD23-0XB0), dc/dc/dc now i tryed to power it up by plugin in the +24v...
Replies
0
Views
1,260
Hello All, I am trying to upgrade the SCADA on site from version 6.0 to version 7.2. I've gone from 6.0-6.2, 6.2-7.0 and finally 7.0 to 7.2 and...
Replies
4
Views
5,441
hello all, im really in a bind here I'm using a micrologix 1100 to send pulses to a stepper driver for a indexing application. What I do is use...
Replies
5
Views
5,823
Hey good peoples, I’m a sparky and do the low level PLC work whenever I get the chance though it has been many years since I’ve done any PLC...
Replies
8
Views
8,233
Back
Top Bottom