High Density encoder input
Brijm
May 2006
St. Marys, PA
645
We have an applications, where we are looking to connect 16 encoders for a simple PLC control. Most of the HSC modules I've seen for AB are 2 channels, and wanted to see if anyone had any recommendations for reading 16 encoders.
It is a simple application 2 Outputs per motor (fwd/rev), with position feedback. Only one motor will be moving at a time, quadrature feedback, with no index....
Any advice appreciated.
there are a few options available to you.
1, switch encoders to the one HSC Card
2. there is a company that manufactures Odd cards for AB - Forgotten name ???
3. if your are using AB VFD's it may be better to input the encoder directly to the VFD and send the position data to them.
Thanks Ian,
These are controlling motor adjustments on a press control. I thought about switching the encoders, but would like to track each encoder individually (in case of undirected movement). All the motors will be a simple starter control, (possibly with softstart) We will have an autoadjust which will turn on the motor and stop it at a preset position (+/- stopping offset) The encoders will also control software limits.
We will be using a RedLion HMI and prefer AB PLC's if required.
Normally this is controlled via the Cieco Press Control, however we are limited to 12 axis adjustments. We would like to keep all the axis controls together, but I am running out of options searching for an elegant way to get 16 counters into the PLC....
Hello all! Have an existing 1769-L18ERM-BB1B V28. with full expansion to 8 modules 1--1734-OB8 and 7--1734-IA4. According to IAB this can not be...
1,887
Hi all 99% of the PLCs I have seen have used 16 point input or output digital cards, in some cases many slots such as 8 cards to make up 128...
51,223
We're having extreme difficulties getting the PLC to recognize the High Density Output Module (C200H-OD218). We're using SysWin 3.4 for...
11,501
Do i have to use interrupt subroutine, or immediate read high speed input, for Unitronics Samba plc or reading only the correponding register in...
144
Can anyone recommend a flexible 600-volt shielded ethernet patch cable? I have used them from Allen Bradley / Panduit before and they are too...
123