Home a Kinetix 5500 Servo using current
1) move the axis toward your hard stop you want to be home. (probably MAJ) (speed depends on what happens when you crash this hard stop)
2) monitor the current
3) when current breaks some threshold, stop the drive (MAS) and then home it (MRP)
This but i would use torque.
Is Torque feedback available on a 5500?
By default it isn't monitored. You have to go into axis properties and check the box for TorqueReference and CurrentFeedback. You will then be able to monitor tags XXX.TorqueReference & XXX.CurrentFeedback. XXX=Axis Name
Also when doing this I've always used a Prox switch close to my hard stop to ensure I'm actually at the hard stop and not reading torque or current increase from a bad spot in an actuator or slide. Many years ago was called in because the homing was off. About an inch before hard stop a bolt had backed out of the linear rail and stopping motion, this increase torque and thought it was home.
Why RA hasn't brought this back into the CIP servo properties is beyond me. As I recall it's an option in the SERCLOSE drives. They do have an AOI for this though which I used on previous project. I recall having to do some tweaking to make it work right. In the end a home-to-torque wasn't repeatable enough for the system we had.
Hello to all.
It's possible to read the current during drive Kinetix 5500 operation and display or capture in the PLC? PLC CompactLogix 1769-L33ERM
OutputCurrent is a standard part of the axis tag. There are a great number of parameters that can optionally read/write from the drive at the coarse update rate by specifiying them in the Cyclic parameters tab of the axis properties.
When I do a "Home to Hard Stop" with Kinetix 5000, I set the torque limits and then use the Axis.TorqueLimitStatus bit to tell that my MVM or MAJ instruction has resulted in the axis arriving at and being stopped by the Hard Stop.
Something I was reminded of the hard way last week is that if you export a *.ACD file to *.L5K text mode and then re-create the project, then the actively-transferred values that come with the cyclic coarse update get reset to all-disabled. At least that's what happened to me on a v32 project.
But the .TorqueLimitStatus bit is automatically updated as part of the ordinary Axis structure, so that wasn't a problem for me. I got tripped up because the bus voltage monitoring alarm was triggering.
Rockwell has an AOI to do torque home for CIP axes. It's a bit buggy and I rewrote it, but you can't just use torque or you will get inconsistent results. You need to set your torque limit to a non breaking value with SSVs, set your position error and velocity error to higher limits to prevent motion faults, also with SSVs, then MAJ until the position error exceeds a soft limit for X time. Once the PE exceeds a limit, then passive Home the Axis to the desired position, and set the torque, position and velocity limits back to normal operating levels. Using this method insures consistent homes everytime, and elimates false homes due to torque spikes.
Hi all, I am commissioning my first servo drive, and I am trying to home my servo but unsure how to go about it. I am programming a gantry...
1,461
I have 2 servos that is moving a gantry. I am planning to use one to follow the other using an MAPC command, but when I home, could I tie the home...
1,386
Does anyone know these drives that can help? I need to move a home position on a drive by -500mm. I've physically got the carrier in position, but...
1,748
The homing watchdog timer preset was changed to 60 sec from 30 sec due to servo homing taking too long. The home offset is around 180 degrees...
1,931
Hi, I am trying to home the Kinetix 300 drive using the home to sensor option, but for some reason:huh: the cam always goes past the home sensor...
4,677