How do I set constants in an AOI?
PLC_Shaggy
Aug 2010
Indiana
I'm trying to create an AOI to simplify my life on some code that we reuse frequently. But so far it hasn't been just a mess.
I have a timer and a string that I would like to remain constant, or the same every time the AOI is used. But once it creates the function online it clears out my PRE in the timer and my string. Both are set as Local Parameters. I want to keep these internal to prevent them from being changed on the floor and to reduce the number of parameters being used in the AOI.
Thanks for any help you can give.
You can set a default value for the AOI's local tags. Click the local tab and enter a value in the default column. This is the value given to the local tag when a tag of the AOI type is created.
Thanks TConnolly.
I went back and tried again. If I created a new instance of my AOI it worked as you said.
My problem was adding logic to an existing AOI. When I added the Timer and String it used the existing data table and left the new items as null.
Hi
I often have a move or cop at the top of the Aoi and just hard code the values in so they cannot be changed but can be seen
Donnchadh
^ I'm with Don, it also makes it easier to trouble shoot and every scan the move will go off and keep your constant forever constant (or at least every scan it will change back).
Note under the 'Scan Modes' tab in the AOI definition you have the opportunity to define other logic. The 'Prescan' may be a place to put 1 time initializations without taking up scan time during the normal scans of the AOI.
Hello, I am using a AB SLC5/05 PLC & using the PID insrtuction for a single loop control. I have assigned N10:0 as the control block starting...
4,979
Hello, I still do not have equipment in to test. But the RTAC ladder does not have a timer reset coil. I wonder if a reset coil on Timer.IN is...
79
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
39
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
19
352
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
107