How I can change NPN to PNP solid state switch?

Steve-r

Member
Join Date
Feb 2022
Location
Toronto
Posts
1
Hi to All,
How I can change NPN to PNP solid state switch?
Exapmle1: D-M9N Solid state switch with D-M9P
Exapmle2: or allen bradley p.e.c. type 42BA S2LNAE-A2 photo switch with PNP model
Just trying to learn if I can switch NPN with PNP sensor to existing PLC AB
Thank you
 
Last edited:
If this is because the PLC input changed from NPN to PNP then just unplug the old switch and hook up the new one. Make sure the output goes to the same wire.



If you only have a PNP switch and have to replace a NPN switch then disconnect the wire going to the PLC input and run it to the coil of a small relay. Then run a Common wire to the relay COM terminal and a wire from the relay N.O. terminal to the PLC input.
 
Welcome to the forum,

As stated above, you can use a relay to switch from NPN to PNP.
If you need fast switching, there are dedicated modules from different brands available to do this [$$$], or search for generic optocouplers on the net [$]
 

Similar Topics

I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
Replies
3
Views
115
Hoping someone can give me some guidance or confirmation of what I need to do. We have a FactoryTalk SE program that I need to change the IP...
Replies
2
Views
92
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
177
Greetings I have a problem, my system is the following: wincc v8.0 (demo), logo8.3, abb m2m analyzer. I created some pages to display the...
Replies
0
Views
67
We had one go down. we have a new one. Their emergency Number don't work. The Model is TLSA046AAH-330N01-007 A catalog says we need software TET...
Replies
2
Views
171
Back
Top Bottom