how many I/O module can be placed in local bank for 1769-33ER?
pittlei
Sep 2019
Chicago, IL
Hi, I am trying to understand in theory how many I/O module I can place in the local bank for the compactlogix 1769-L33ER .
the bulletin says max Local Expansion Modules Supported is 16.
the power supply must be within 4 slots of controller.
the maximum distance between the I/O module and power supply is 8.
can i place the modules like way below?
controller|IO1-3|Power supply|IO4-11|end cap
in this way, I can place 11 I/O modules in the local bank?
thanks
Yes that is how I have done it in the past. After that you will have to add another power supply and then IO12-16.
The limitation is in the modules themselves, each of which have a power supply distance limit. The CPU has a distance rating of 4 (i.e. 3 I/O modules between controller and power supply), which is why you can only have 3 modules to the left of your P/S. To the right, you can have as many modules as the controller can support, as long as you don't exceed any of those module's distance ratings.
Most modules have a distance rating of 8, so as you suggested, you can *usually* put 8 modules to the right of your power supply. A notable exception is the 1769-OB32 which has a distance rating of 6. Some specialty modules also have lower ratings.
Once you exceed the distance rating, you have to use a bus extension module, and make a second bus with its own power supply. As you don't have a CPU on the second bus, you can theoretically add 8 modules either side of the P/S on that bus, for a total of 16 additional modules - again, as long as you don't exceed any one module's distance rating, and as long as you keep within the total module limit of your controller.
Also, you have to make sure you do not overload your power supply. There are two different capacity supplies and cards power consumption varies.
The easiest way to make sure everything will work is use Rockwell's free Integrated Architecture Builder software and configured the cards in it. It will tell you if a card has a different distance rating or if you overload your power supply. It will also give you the part numbers for the expansion endcaps if you need.
Building a CompactLogix is a nice feature of the Integrated Architecture Builder (IAB) program. It will help with power supplies as well. You can get it from your distributor.
Good Evening , We have a number of Powerflex 525 Drives . I took notice for years elsewhere and our plant , that our Powerflex 525 drive...
640
Good Afternoon, Just wondering , are many of you using SAP in your plants ? If so , is it difficult to learn ? Are there many training...
1,420
It better to have too many instead of not enough right?
26
2,895
Hi all- I have an application where: - I have a fixed system with a pre-determined, static, network (say, 192.168.2.0/24). - That system...
4,239
I have an application that needs 20 inputs and 20 outputs with only 10 XNOR and 10 NAND blocks. I could do it with relays, but this could end up...
5,172