pittlei
Member
Hi, I am trying to understand in theory how many I/O module I can place in the local bank for the compactlogix 1769-L33ER .
the bulletin says max Local Expansion Modules Supported is 16.
the power supply must be within 4 slots of controller.
the maximum distance between the I/O module and power supply is 8.
can i place the modules like way below?
controller|IO1-3|Power supply|IO4-11|end cap
in this way, I can place 11 I/O modules in the local bank?
thanks
the bulletin says max Local Expansion Modules Supported is 16.
the power supply must be within 4 slots of controller.
the maximum distance between the I/O module and power supply is 8.
can i place the modules like way below?
controller|IO1-3|Power supply|IO4-11|end cap
in this way, I can place 11 I/O modules in the local bank?
thanks