Go ahead, hook up your thermocouple.
But you won't get a room temperature reading, you'll get 0mV, which, if you convert the 0mV to a temperature according to the thermocouple tables, you'll get 0 Deg C, the freezing point of water. That's exactly correct and it is NOT a problem with the PLC, its analog input card or the thermocouple, it's just the wrong way to read a temperature.
A thermocouple measurement actually requires two temperature measurements
- the mV gradient across the thermocouple (hot end minus cold end) and
- the temperature of the connection terminals, also known as cold junction or ice point compensation.
At room temperature, both ends are at the same temperature so the temperature gradient across the thermocouple is non-existent. Hence, the EMF output is 0.0mV.
You can test this by putting a voltmeter across the wires of thermocouple sitting on your workbench or desk. The reading will be 0.0mV, because there is no temperature gradient; there's no difference in temperature to generate an EMF.
Your attempt to make a thermocouple-only measurement with a DC volts AI card (assuming you do the work to convert to temperature), will always have large negative offset error, of about 15-10 Deg C. It will always read low by the difference between terminal block temperature and the freezing point of water. At room temperature, it should and will read 0 Deg C.
It is the cold junction (CJ, or ice point compensation) circuit on a thermocouple card that measures the temperature of the terminals (usually close to room temperature) and that CJ signal gets added to the thermocouple signal for a conversion to temperature.
So a temperature reading by a thermocouple card is the cold junction temperature measurement PLUS the thermocouple reading.
At room temperature, when the thermocouple is 'isothermal' (no temperature difference), its output is 0mV (the freezing point of water on the thermocouple tables). 0mV = 0 Deg C.
You need either
- a thermocouple input card to use your J thermocouple as direct input, or
- a temperature transmitter for a J type thermocouple which provides a linear, high level (4-20mA/0-5V/1-5V) signal that is compatible with your AI card.