How to connect thermocouple to a PLC input module

There are only two terminals in the sensor box. I will attach pic for it
Screen_Shot_2015_04_18_at_5_06_53_PM.jpg
[/url][/IMG]
 
What I pan to do is connecting the two terminals that the sensor has directly to the analog input device (to +inCh0 and -inCh0 ), After that I will try to do normalization and scaling.
 
As bit bucket says, none of the sensors appear to be Thermocouples. Can you tell us which one you have (model no.)

Steve
 
Thermistors - AAARGH! More inaccurate than thermocouples! Also harder to scale. Forget it and buy a 3 wire RTD and input module. 2 wire are also inaccurate and there is no resistance compensation wire. One has to be careful with thermocouples as well as the output will vary along the distance of a cable as it passes through different temperatures. Thermocouple compensation cable must be used. Additionally any terminals used along the way should be of the same material as the thermocouple wires - this means different terminals for the 2 wires.
 
Oh dear, it's not going to be as easy as you think.
First we need to know the PLC type, basically I'm not sure of any mainstream PLC's that accept a direct thermistor input, analogue cards generally accept 0-5V, 0-10V, 0-20mA or 4-20mA inputs.
I would therefore suggest that you need a signal conditioner or amplifier that accepts thermistor inputs and converts it to one of the analogue cards input signal levels.
Others on this forum may have another solution.

Steve
 
All I did is use a J or K thermocouple, attached it to a 4-20Ma Thermocouple transmitter and from there to my analog input on my SLC-500.

Then I used the SCP instruction to send it to a N file which was the reading in Celsius so I had to add a couple of rungs to convert that to Fahrenheit and sent it to another N file which I am using for the tag address on my HMI.

I have been using this at home for the past 2 years with out issues.
 
Rashwan Mzhr ...Please use this before I have a stroke


The LM34 device does not require any external calibration or trimming to provide
typical accuracies of ±1/2°F at room temperature and ±1-1⁄2°F over a full −50°F to 300°F temperature range.

Operates From 5 to 30 Volts ........PLC analog range
Less Than 90-μA Current Drain



$2.30 .......cheaper on ebay

http://www.newark.com/texas-instruments/lm34dz-nopb/temperature-sensor-1f-to-92-3/dp/41K4759?mckv=s1pV1qEmc|pcrid|57087234021|plid|&CMP=KNC-GPLA?gross_price=



easy to use:

http://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&ved=0CB4QFjAA&url=http%3A%2F%2Fwww.ti.com%2Flit%2Fds%2Fsymlink%2Flm34.pdf&ei=g6IzVZanCcSzggTTw4CgAg&usg=AFQjCNGV4NvgDOVcwjl9a-zCnWiDRuAnfQ
 
Last edited:
Rashwan Mzhr ...Please use this before I have a stroke


The LM34 device does not require any external calibration or trimming to provide
typical accuracies of ±1/2°F at room temperature and ±1-1⁄2°F over a full −50°F to 300°F temperature range.

Operates From 5 to 30 Volts ........PLC analog range
Less Than 90-μA Current Drain



$2.30 .......cheaper on ebay

http://www.newark.com/texas-instruments/lm34dz-nopb/temperature-sensor-1f-to-92-3/dp/41K4759?mckv=s1pV1qEmc|pcrid|57087234021|plid|&CMP=KNC-GPLA?gross_price=



easy to use:

http://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&ved=0CB4QFjAA&url=http%3A%2F%2Fwww.ti.com%2Flit%2Fds%2Fsymlink%2Flm34.pdf&ei=g6IzVZanCcSzggTTw4CgAg&usg=AFQjCNGV4NvgDOVcwjl9a-zCnWiDRuAnfQ

Nice device....I will have to test one of these.
 
Rashwan Mzhr ...Please use this before I have a stroke


The LM34 device does not require any external calibration or trimming to provide
typical accuracies of ±1/2°F at room temperature and ±1-1⁄2°F over a full −50°F to 300°F temperature range.

Operates From 5 to 30 Volts ........PLC analog range
Less Than 90-μA Current Drain



$2.30 .......cheaper on ebay

http://www.newark.com/texas-instruments/lm34dz-nopb/temperature-sensor-1f-to-92-3/dp/41K4759?mckv=s1pV1qEmc|pcrid|57087234021|plid|&CMP=KNC-GPLA?gross_price=



easy to use:

http://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&ved=0CB4QFjAA&url=http%3A%2F%2Fwww.ti.com%2Flit%2Fds%2Fsymlink%2Flm34.pdf&ei=g6IzVZanCcSzggTTw4CgAg&usg=AFQjCNGV4NvgDOVcwjl9a-zCnWiDRuAnfQ

The PLC range that I have 0 to 10 V. so, I guess the device that you suggest doesn't work. Thanks
 

Similar Topics

This question is about a Q68TD-G-H01. When I disconnect the thermocouple connected to channel 8 of the module, I am expecting D111.F to go TRUE...
Replies
12
Views
3,490
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
49
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
333
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
121
Back
Top Bottom