Its sounds like you got a lot of responses. I just want to make a correction to my earlier post.
I said that we have an application the uses an analog module. I did some digging. As it turns out we have a universal analog input module. 1746sc-ni8u which can be set up to do voltage, amperage, rtd, or thermocouple input. The input into the program is a temperature. We then manipulate this number through some math functions and run it through a PID function. The resulting number is then outputted to an actuator.
The voltage generated by the thermocouple is really low. For a type j thermocouple 368 degrees only generates 10 mv. Each degree change in temperature results in like 0.025 (roughly ...its not linear) mv increase. So without any sort of signal conditioning it would be very difficult to do with a normal analog card.