How to Convert Hex To String
RRoc
Jan 2017
California
45
I'm trying to display a Allen Bradley Controller Serial Number that's in HEX to String for my SCADA to display.
Any ideas?
Yes I'm trying to do that inside my PLC so my SCADA Programmer does not have to worry about it.
I saw that thread. I'll look at it again.
Looks like he is masking the sint storing the result in temp and converting to ASCII equivalent
so for example 1F
first mask takes just the '1' portion
Xf0
ie mask is 1111 0000
result is 16#10 or 16
/16
gives 1
add 48
gives 49
which if you look up in ascii table is '1'
store in string
next mask you original SINT 1F
0x0f
0000 1111
result is
16#0f
or 15
add 48
gives 63 however ascii table 0-9 is 48-57 and 'A-F' is 65-70
so since our result is > 57 add another 7 to make it 70 in this case which happens to be ascii 'f'
so result is ascii '1' and ascii 'f'
hope this helps
ascii table http://www.asciitable.com/
Hi I need to convert a DINT with HEX value e.g A0F15663 to a string with the same value 'A0F15663'. Any tips of good instructions to use ...
3,403
We are doing some testing communicating serially with a linear actuator in order to get its current position using an Allen Bradley Compact Logix...
21,181
I actually solved this, but I thought this info may help others. Condition which prompted this need: I was using a function provided to me by...
3,756
Hey All, i have been fortunate enough to play around with an Applied Motion Products Servo Drive SV200 with 100 watt/ 24vdc congif. I managed...
1,893
Good morning, I am running a controllogix and I am connected to a hydrocarbon gas alalyzer over an EWEB module. I am picking up a Hex number...
40
13,939