How to UPLOAD hardware cinfiguration to PC un SIMATIC STEP7

ifnul

Member
Join Date
Nov 2013
Location
South Celebes
Posts
9
Hi everybody,
Does anyone know how to upload hardware configuration from PLC to PC in SIMATIC STEP7. I'am using S7-400
does it make the plc stop when I upload?
thanks for the kindly answer
 
- The PLC doesn't stop when you upload.

- To get online, try this:
In HW-manager you must insert a rack and the cpu type.
If you connect via the PN-interface, you must put in the IP-address. If you use the MPI-interface, you must put in the correct node number, default is 2.

Now you just click on the upload icon. You'll be asked for a project name, and the online hwconf. will be saved in this project.

This is taken from my fainting memory, hopefully you'll be helped.

Kalle
 
- The PLC doesn't stop when you upload.

- To get online, try this:
In HW-manager you must insert a rack and the cpu type.
If you connect via the PN-interface, you must put in the IP-address. If you use the MPI-interface, you must put in the correct node number, default is 2.

Now you just click on the upload icon. You'll be asked for a project name, and the online hwconf. will be saved in this project.

This is taken from my fainting memory, hopefully you'll be helped.

Kalle

i have tried connect by using MPI,
There are to option of target station :
1. Local
2. Can be reached by means of gateway
first, i choose option 1, then it doesnt work becouse cant establish connection
then i choose option 2, but the program ask me to input address and S7 subnet ID. how do I know the address an subnet ID of the station??

Thanks for your help
 
Upload a PLC

In addition to what migwib have said, you should know the MPI address of your CPU(provided that you are communicating via the MPI port & that you chosed MPI in your SET PG/PC Interface).

To know your MPI address you chose DISPLAY ACCESSIBLE NODES from the PLC Tab).

If all of the above is set correctly , then you should be able to upload your CPU.

Cheers
Hagos
 
In addition to what migwib have said, you should know the MPI address of your CPU(provided that you are communicating via the MPI port & that you chosed MPI in your SET PG/PC Interface).

To know your MPI address you chose DISPLAY ACCESSIBLE NODES from the PLC Tab).

If all of the above is set correctly , then you should be able to upload your CPU.

Cheers
Hagos

Ok, It's Work
Thank You Very Much 🍺
 

Similar Topics

Goodday! I have a Fixed Hardware SLC500 (1747-L40a) connected to 1747-DTAM. Can someone help me upload the program from it? Trials: 1. 1747-AIC...
Replies
6
Views
5,713
Hi all, I've got a strange problem on one of our old S7-315's. There are no error LEDs on the PLC and it runs fine. I have a project on our...
Replies
5
Views
9,474
Hi all, just have a theory question here. Using step7 5.5. I upload the hardware configuration from a dp or pn network that i do not have the...
Replies
3
Views
3,174
Please help me How to B&R 7CP476.60-1 upload program Backup and download which program should I use. Pvi transfer tool.? And how. Thank you
Replies
0
Views
88
I HAVE A OLD MESSUNG HMI AND I WANT TO UPLOAD A PROGRAM FILE FROM IT TO A USB PENDRIVE WITHOUT USING PC OR SOFTWARE...WHAT SETTINGS I HAVE TO DO...
Replies
2
Views
83
Back
Top Bottom