so I have this (temp +relative humidity) sensor ( pfmini72) from mitchell instruments , the sensor works fine for temperature reading but when it comes to humidity it gives a reading of -378, -360, -342 and so on never crossing 0 , I connect the plc to a pc so that I can monitor the program that's how I can see the readings. it only moves by +18 as you see and these readings don't have a pattern so that I can modify the program, I know there is no pattern because I have a humidity measuring device a calibrated one and when it gives 20% RH , it gives once -378 and another time -360 and -342 and so on for the same value of RH and while the calibrated device keeps moving up and down in the RH measurement , the reading of the sensor always oscillate between two values , I mean it gives -378 reading for 20, 19 , 18,... 10% RH and so on. so the sensor output is 0-1 v for 0-100% RH so I disconnected the sensor from the plc and started to measure voltage from the sensor o/p and it gave correct o/ps like when it says .32 v, the measurement of the calibrated device is like 30 % RH which is very close and it's like that for all values of RH I encountered , so I don't think the problem is in the sensor. so I changed where I put the RH o/p of the sensor in the plc to the one that's connected to the temperature o/p but it's still the same. P.S. the plc is LENZE.
so any help would be greatly appreciated as I don't know how to deal with this humidity output, thank you.