Gents, first, thanks for the wealth of knowledge on other questions it is much appreciated. My new question is, I have a HV supply with readings of Watts, VAR and amps into my PLC, can anyone point to a formula that can help me calculate the LV side current.
THanks in advance, Steve D
actually, I was wondering if I had to take into account the efficiency (VAR) when calculating my LVA. I can make a PLC take off its pants a waggle its thing but I can't remember 1st year apprenticeship stuff, such is the dumb questions of a specialist.
Steve,
The eff of the device used for voltage conversion (maybe a transformer?) may be negligable. If you explain the app a little more someone may be able to help you with that issue.
BTW, Bookmark the link I sent you. Great reference for thoes times when the brain shuts down.
Also..Join the club & register on the forum.
Best regards, Mike
VA to VA conversions are constant.
KVAR are the vertical components of the two power triangles.
KW are the horizontal components of the two power triangles.
The diagonal are the KVA, and the resultant of the other two vectors.
The efficiency of the transformer is a heat loss issue, and would be accounted for as KW in the HV side, but would still be present in the VA portion of both sides. You won't lose Watts without associated amps. KVAR will not affect the KW at all, except as it relates to additional VA current, which will cause more KW loss, but you will not be able to separate this component of the KW from the "load" component of the KW without specifically trying to isolate it with temperature measurements. Regardless, it will not be KVAR, but KW, anyway, if it causes heat. (Short form of the previous: Extra amps that cause heat are KW, not KVAR, no matter what caused the extra amps to flow).
The KVAR's are needed by the load for magnetization and charge (plus and minus vars), and have absolutely nothing to do with efficiency, but are integral to power factor. Power factor has absolutely nothing to do with efficiency, except as noted above/causing more amps.
If this doesn't help, perhaps you could specify your need for information a little more, and we'll try to help.
Don
I'm stumped by something seemingly simple. I want to move the numerical value of an ASCII style SINT into a REAL tag in Studio 5000. What's the...
64
I’m running short on time to complete this project (retirement looming), so thought I’d ask here hopefully save me some research time. I’m...
88
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
233
Currently I’m using ESA model VT155W0000 HMI and it’s communicate with Fanuc PLC. Can any one suggest can I convert ESA model to EXOR HMI eSMART07M
123
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
153