I have a PanelView Plus, possible to show historical data?
plctek
May 2022
toronto
23
If I have a PanelView Plus, is it possible to show historical data via historian on it?
I have the application all setup in FT Studio Machine Edition, ME, but there doesnt seem to be an option to add a historian like there is in SE
More than likely, your PanelView Plus is just visualization for a PLC.
You would configure Historian to collect the data from the PLC, not the PanelView Plus.
The PanelView Plus likely serves as a visualization interface for a PLC. For data collection, configure Historian to gather information directly from the PLC, not the PanelView Plus.
I assume you want the historian for showing data in a trend.
FactoryTalk View ME / PanelView Plus doesn't support a historian. They have a "Data Log" function that is used for trending. It is not on par with an actual historian but for trending purposes it does an OK job. Unlike SE though you can only have one Data Log Model. So you can't turn it on and off and start and stop different models as needed. There is one model and it would run all the time.
OG
Hi, was wondering is it possible to remotely connect to a Panelview Plus 700 from a laptop with RSstudio software i.e Modem?? etc. A client just...
6,303
82
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
56
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
85
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
93