Why is that? If I leave it the way it is will both outputs be active at the same time on the 40th. second? If thats true then I will haft to go through and refigure all my numbers again! ?$%#?@#^@^%##$%()*Lancie1 said:If you are using the LIM instruction, then (because it switches when equal to Low Limit), you must not allow any overlap in your lights.
For example if E/W Red = 0 to 40, then E/W Amber must start at 41, not 40.
Thanks for the help. Dennis