IBHLink S7++ / CP 342-5
alextroto
Jul 2022
bucharest
I'm trying to develop a software which should read tags from a Simatic S7-314 / CP 345-2. For this I'm using S7.NET + c#.
I'm using a IBHLink S7++ gateway between the profibus and ethernet networks. If I'm using the MPI interface of the CPU, everything runs as expected. But If I'm connecting to the profibus interface from the CP 345-2, I cannot read anything from the PLC DB.
Any ideas what could cause the problem?
Thank you,
Alex
Can you see the CP when you go to the diagnostics page as shown at the bottom of this wiki page:
https://wiki.ibhsoftec.com/en/IBHNet:IBH_Link_S7
In you application, are you setting the correct rack/slot configuration ?
I believe that the principle is the same for DP as for MPI
https://wiki.ibhsoftec.com/en/IBHNet:RFC1006_Communication_IBH_Link_S7++/S7++HS
So if for example the CP has DP address 5, you must set Rack = 0, Slot = 5.
N.B. going via a Profibus CP in the S7-300 rack actually doesnt give you any advantage.
The data still have to pass via the MPI bus that is in the backplane of the S7-300 rack.
With such an adapter you can just as well use the MPI port in the CPU.
Hi Jesper,
Yes I can see the CP in the diagnostic page. Moreover, I can setup the IBH Link on PG-PC to manage the S7 station. Also, I'm entering the right rack/slot DP address for the CP. If I'm entering a wrong DP address, I cannot connect at at all, I have another kind of error message.
I need to use the profibus/CP 345-2, because the S7 is already in production, unfortunately I cannot change the architecture.
You dont change the architecture if you put the IBHlink on the MPI port of the CPU.
If the MPI port is already used, then plug the IBHlink first, and then plug the existing MPI cable on the piggy-back port on the IBHlink.
Has anyone got any experience with Ethernet-mpi IBHlink & tia portal 14 or newer I have it working fine in simatic manager but in tia, although...
1,927
I use s7 IBHlink to connect serval PLC's.I use the IBHlink for MPI in Wincc. My problem is that i have to chose between the serval plc in set...
1,619
Dose anyone have experience with Beckhoff FC3121 profibus master PCIe card connected to Siemens CP342-5 as a profibus slave? The data retrieved...
17
4,810
Hello I have a DC motor for a conveyor that I controll usind EL7342 beckhoff drive and AtmoSingleAxisDrive object from OES. The thing is I can...
4,998
Hi Ali, I'm setting up comms between DeltaV as master and S7300 cpu315-2 as slave. I have already comms using 1 cp342-5 bet this not...
2,420