Instruction Reset

Huybm

Member
Join Date
Jun 2016
Location
Ho Chi Minh City
Posts
5
Hi everybody!
Im meet a problem with reset instructions. I must reset about 200 contactscontinues from m10 to m210, this is my program:
.....
...rst m10
...rst m11
...
...rst m209
...rst m210

I dont know how to shorten it, please help me, thanks!
 
Welcome to the forum, you don't say which PLC you are using, but if its a mitsubishi then you can use the zone reset function. [ZRST m10 m210]
Otherwise we need more infomation.
Steve
 