Intermittent comm problem CompactLogix, PV+

Hello. After many trips back to the customer site it turned out the plant maintenance guy (aka Bubba) was going online after I left and forcing the speed of the Ethernet port to 10Mbps. That is what was causing the issue. Switched it back to Auto and everything was fine after that.
 