Invensys Analog Input card
bayeibrahima
Sep 2010
DAKAR
188
Hello
I have a Transmitter (reading conductivity of Acid tank of CIP Station) connected in an INVENSYS analog input card
I get some values in local (on the Transmitter screen; Model E+H Liquisys CLM223) but dont have any result on my Supervision pc (it shows 0°C while on the transmitter it shows 67°C)
I have no docs for the module and I would like to know how the analog processing value is done with this kind of module
I do need your help
Hope to read you soon
Best regards
Hello Cornbread
unfortunately; the module is presently in a running process and I can't stop and get it out from the panel
There's no indication in the front side (perhaps in the baseplate side); but the Profibus Card in which the analog module is connected is Allen Bradley model (FLEXI/O PROFIBUS Adapter module Cat.No.1794-APB Series B)
I want to plan a General Maintenance for the hole CIP Station and need to get informations about the module before stopping
Best regards
Are you sure it is an Invensys analog module? If it is installed within a 1794 FLEX I/O Rack it has to be an Allen-Bradley module.
Find out the Catalog Number of the respective module and then navigate to:
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1794-um062_-en-p.pdf
or
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1794-um008_-en-p.pdf
depending of the module at hand.
The Catalog Number is listed on the front of the module (1794-XYZW...)
ºC ???
If the transmitter is reading conductivity of the acid tank, it should be mS.
the Model E+H Liquisys CLM223 can also have the temperature as a second analog output, but you did not mention if the conductivity was OK.
Is the temperature analog Output also wired to the analog Input card?
Sometimes we only connect the conductivity Output.
Hello thank you for your different post
The Transmitter displays both conductivity and temperature; because the detection cellule has a Pt100 sensor in
On supervision pc we get conductivity reading (2.3 ms which is very different to the value displayed on the Transmitter) while for temperature we get 0° (67° on the transmitter)
The company that supplied the system uses an Invensys plc and in all modules it's mentioned "INVENSYS", that's why Ithought it's an Invensys module
Best regards
Hello Cornbread
Best regards
Your Invensys CPU is Profibus controlling a Remote Rack consisting of an Allen-Bradley 1794-APB Profibus communications adapter and various 1794-XYZ Allen-Bradley modules, one of which is the Analog Input module you are inquiring about.
Find out the Catalog Number of the respective module and follow the links I have previously posted for in-detail technical information.
Hello dmargineau
yes; that's exactly what you said;I've already downloaded the docs from the link you've given and I'm reading it
thanks in advance for your help
Best regards
Hello to all; my problem is not solved yet
I've read the docs, but don't still find any solutions in them
please can someone has another ideas
Best regards
Hi Everyone, Currently, I am facing with a problem about analog output module with PLC trident of Invensys . The module sometime generate a fault...
1,281
Does anybody have experience with such devices: Which software should I use to work with it? Do I need any specific cable to connect it? Is it...
3,473
I have inherited Invensys Wonderware SCADAlarm scheduling due to an employee leaving. I've learned enough to have a bit of knowledge, but have an...
1,382
Greetings everyone, I'm looking for a pinout/wiring diagram for the AUI adapter cable part # P0970XF. Much help would be greatly appreciated!
1,255
Greetings everyone, I'm in need of the Foxboro I/A series System Equipment Installation Manual document number B0193AC. I've looked all over for...
2,364