IO status from protected Siemens PLC

blaze_george

Member
Join Date
Feb 2020
Location
Dubai
Posts
1
I have a password protected Siemens ET200SP PLC, with 'Permit access with PUT/GET communication from remote partner' option disabled.

Is there any way to take the analog input module readings to a third party device like Ew*n Flexy? Modbus, any external software running in windows, through HMI, anyhow.
 
I'm assuming you don't have the password. Does the device have the web page activated, OPC UA, anything like that?


There is no way to get the PLC data that can't be locked out by security settings in one way or another.


If you want the analog input readings, you might need to tap them. Obviously the wiring/electronics required varies depending on whether they are voltage/current/temp/etc.
 

Similar Topics

I am working with a remote rack with a 1771-ASB adapter, and inside Logix 5000 I am trying to find where it displays the status of each of the...
Replies
8
Views
119
Hello, I'm working with Studio 5000 and ME Station, and I'm trying to find a way to detect if the PC with the HMI is shut down or not. I've tried...
Replies
5
Views
140
Hi I have a ifix 5.5 application where the operator opens a valve by clicking on a screen object. I can trace from object to data base that it is...
Replies
2
Views
64
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
72
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
Replies
3
Views
202
Back
Top Bottom