Is it possible to link ML1500 and PV1000+ by 1761-NET-AIC+?
bundhit
Sep 2003
Bangkok
39
I have ML1500 and PV1000+. I would like to display the
parameter value in the ML1500 on the PV1000+. The following configuration is impossible or not, please suggest or
share your experience
[ML1500]----DF1----[1761-NET-AIC+]----DH485----[PV1000+]
......................................[Laptop]
Do the 1761-NET-ENI module instead. It will allow you to use the Ethernet functionality of the PV+.
You can connect directly, just as with the NET-AIC module but will allow for way more in the future. (And costs about the same)
If you connect your laptop when Pv+ in Dh485 network you will not get the correct data & you may face many timeout for online programming better go with Ethernet Network as SNK
Thanks & regards
Praveen
Bundhit,
Refer to this post where I had a similar issue. Your arrangement should work but I would not recommend connecting the AIC+ directly to the laptop. There is a driver in Linx that supports this but it is outdated and unreliable. I would suggest getting a 1747-UIC interface which would allow you to connect via the USB port and use the standard RS232 driver in RXLinx.
-John
Thanks to all opinions,
It's worked already!
My above configuration is wrong because the Ch0 of ML1500
was set as DF1. So, I could not read the data.
I corrected to DH485 and it worked finally.
[ML1500]----DH485----[1761-NET-AIC+]----DH485----[PV1000+]
Sorry, it was really obvious wasn't it?
But really, the next time, use the Ethernet Module. It will allow for better expandability later.
In the past when testing a particular HMI with a CLX program I'd use rsemulate with rslinx virtual backplane driver and create a dde topic for the...
2,157
Hi all I have a project that uses a Siemens 315-2DP and two HMI's. The two HMI's are at separate ends of the line. One of the HMI's has a...
2,952
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
221
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
353
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
185