Is there a simple way to configure 1769-HSC?

briana banks

Member
Join Date
Jul 2005
Posts
242
Hi All

I've read the manual...didnt understand much...

I have a accurate flow meter that gives pulses with certain width.
just have to obtain the rate from the HSC.

Thanx
 
Are you using it with a Micrologix or Compactlogix?

You need to set it up for frequency mode but need to know which one for the specifics
 
Hi

I have read the manual.

I know i get the pulse input in B1
i dont understand the remaining.
I need to get the rate and quantity
 
Set the operating mode of the counter to "Pulse Internal Direction". Leave the scaler at zero. This should give you pulses per second to start with, then we can work on your scaling

The LED indicators are turning on and off with the flow meter pulses aren't they?
 
Hi

Using rslogix 5k ver 15.

"Pulse Internal Direction" what does it means? what are the 3 other options?

if i get the pulses in Local:4:I.InputStateB1
where do i get the rate i.e. pulses per second (which paramter)?
where do i reset the counter?
How do i cofigure the HSC to count the pulses and obtain
the quantity.


Thanx
 

Similar Topics

Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
174
Hi all, Writng a FB in ST on Beckhoff TC for a pulser which turns on and off on a cycle, is paused by turning bControlInput to FALSE, but resumes...
Replies
6
Views
262
I'm trying to build my Classic Step 7 programming skills this weekend. I get stuck on little things that are not covered in YouTube tutorials. I'm...
Replies
7
Views
321
I have a program that does a 7 second "scan" sensor calibration routine whenever a setting (setting is called assistance level or "AL" and ranges...
Replies
3
Views
217
Hi all, I have a simple question that I have overcomplicated and gotten stuck on. I have a variable, we can call it "light" that I need to stay...
Replies
4
Views
323
Back
Top Bottom