Isolate current signal

Pandiani

Lifetime Supporting Member
Join Date
Apr 2005
Location
Tz
Posts
718
Hello guys,
I'm not sure if I used correct term in the topic's name but basically I need the following.
I have one pressure transmitter that gives current signal (4-20 mA) and I want to use that signal on two places:
1. as input to analog PLC card
2. as input to instrument
I know I can just put instrument in series and everything is fine. Actually that is exact way how it is done now. I need some way to isolate this signal so I have one "part" that goes to instrument and other "part" that goes to PLC so I can safely replace instrument in case of need without disturbing PLC.
I hear that there is some kind of galvanic isolator circuits but not really sure.
Can you suggest me solution for this problem?
 
A quick solution, if possible, is to use an instrument with a 0-5 VDC input. Chart recorders and so on are often available that way. Then you just put a 250 Ohm resistor across two field terminals. The recorder can be removed at will without disturbing continuity.

Another trick I've use is to have a reversed Zener diode across the instrument terminal. When the recorder is pulled, the diode conducts. You have to make sure the voltage and current rating of the Diode are consistent with your instrument.
 
Thank you guys, I'll check these links. Tom Jenkins, I like your suggestion about Zener diode...
 
I'd say no.

If channel 2 is the same as channel 1 and terminal 43 is internally grounded (as is terminal 41) then you've effectively shorted channel 2 input.


Kevin H
 
Thank you for your reply krk.
Yes, internal ground was my dillema too, that's why I post this attachment.
What would you do in this situation? Can I use this type of isolator at all?
I was thinking to use two separate devices whose input would be connected in series but not really sure about this.
 
Last edited:
Ideally you need a signal multiplier for this application.

The 28 14 86 7 is a Phoenix Contact device that would do the job. (data sheet attached)
 
Yes, it seems it's just what I need.
Besides that, I think that using two isolators should do the job.
In other words, I can't think any reason why solution in new attachmnet wouldn't work.
 
As long as the transmitter can handle the combined input load it should work OK
 
KRK's Phoenix Contact solution does the job with one single module that provides two isolated outputs, rather than using two, separate isolators.

Dan
 

Similar Topics

Need advice! We have a powder coat line controlled by 4 DL06's networked together. Each unit controls a segment of the process, the conveyor, the...
Replies
5
Views
2,236
Hi friends; I want to isolate the magnetic pickup sensor but i do not know how? Actually i have Magnetic pickup which provide me maximum 15 volt...
Replies
0
Views
1,653
I haven't posted this before since I was waiting for the investigation to be complete. Last week, one of our operators decided to clean a...
Replies
7
Views
2,582
Today I was working on my project for school and we were using a power supply with 24V and we accidentally had the current at 0.9A. We heard a pop...
Replies
9
Views
558
Hi all, I have been working on a project that requires me to measure the current across a 90 VDC motor of a medical device (similar to an...
Replies
26
Views
1,573
Back
Top Bottom