Issue with CPU318, hardware interrupt and CP343-1 Lean card

uptown47

Lifetime Supporting Member
Join Date
Feb 2008
Location
Over there, next to those boxes
Posts
1,146
Hi all,

I'm trying to fit a CP343-1 Lean card (v3.0 6GK7 343-1CX10-0XE0) on to an existing rack that has a CPU318-2 (6ES7 318-2AJ00-0AB0) in slot 2 and a input interrupt card (6ES7 321-7BH00-0AB0) in slot 4.

Initially I dropped the Lean card into slot 5 but found that the lean card wasn't working. I thought it could be a fault backplane etc so tried swapping the interrupt card and back connectors with spares but to no avail.

I then put the lean card in slot 4 and the interrupt card in slot 5 and the lean card worked. Unfortunately then the machine bombed out on a error to do with it's clock pulse. I think the error is because it isn't getting it's clock pulses quick enough. If I 'inch' the machine slowly it all works fine.

The addresses haven't changed on the interrupt card and I can't see anything that would effect its functionality by being moved into a different slot.

Has anyone got any ideas on what might be happening here? Could the 'lean' card be slowing the backplane comms down so much as to make the interrupt card not work?

Or does the interrupt card *have* to be in slot 4?

Or is there any other reason you can think of why this configuration wouldn't work?

Many thanks

;-) :unsure:
 
How You use Lean in S7 program?
Have You Connections for it and what is slotaddress "W#16#????" there and in S7-call?
 
Hi Seppoalanen,

I'm not using the lean card in the program at the moment. Eventually it will be used by a PC to retrieve some DBWs out of the PLC. I've done this on some other PLCs and it has been fine. The only difference with this one is that it's a 318-2 and there's a hardware card.

Thanks ;-)
 

Similar Topics

I am kind of new to GE products, but we have several in my area. I made a minor logic change and it verified good, but when I tried to download I...
Replies
5
Views
39
Hello all, I am currently facing a problem with a Pro-Face HMI PS5000 project file download. I have tried using GP-ProEX SP1 (4.09.350) and...
Replies
0
Views
26
Hi there, Throughout testing I have made small changes and tested them on PLC sim. I don't have the S7-1200 or any hardware yet so have just been...
Replies
2
Views
72
I've been dealin with some intermittent CIP explicit messaging issues. I tried reducing the amount of small MSG instructions and converted them to...
Replies
7
Views
135
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
54
Back
Top Bottom