issues with devices in ethernet Network of controllogix system
dingomex3
Mar 2012
mexico
33
Hello guys, I have a network card ehternet 1756-en2tr configured in linear mode , not ring mode. And in RS Linx I can not see the devices that are connected to this card but in the RSLogix 5000 controller tags the tags associated with these devices appear. The question is why do I not see them on the network by rslinx?
I attach pics about the problem
Error_8609-0.jpg Error_tags_se_ven_pero_NO_modulos.jpg Error_tags_se_ven_pero_NO_modulos_1.jpg
What are the devices? There are no EDS files loaded, so I would expect to see a 1756-MODULE generic type with the I/O/C configured properly. Your I/O/C seems to be 0 for everything.
Hello Mr rdrast, I think you're a very smart person, so I hope you can help me to solve my problem. I Already Installed the EDS files of 1756-EN2TR. However when I try see the devices (devices like drives, Guard I/O, Flex I/O, and others) that are linked to this module, I can't see them, but I can see all the tags linked to this ethernet, I just see the yellow ask symbol.
You need to install the Add-On Profile for the 1756-EN2TR module, not just the EDS file.
These Add-On Profile (AOP) files are downloadable from the RA web support site:
https://download.rockwellautomation.com/esd/download.aspx?downloadid=addonprofiles
Use and ordinary Control-F FIND search to find the 1756-EN2T module profiles on that page. Check the box for that AOP, download it, and install it using RSLogix 5000.
Ken, Thank you so much. I have installed the Add-On Profile and you have the true, you're "una pinga" like we say in Mexico. That means you're the master of masters hahaha!!!
Thanks Again!
Programa_after_install_AddonProfile_1.jpg Program_After_install_Addon_profile_2.jpg
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
169
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
159
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
70
I have an Allen Bradley temperature switch that I am trying to use in studio 5000. I am getting the message "Unable to interpret the IODD file"...
101
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
272