Kepware OPC server multiple devices
TFBest86
Aug 2010
San Antonio
I'm hoping someone has some idea, what kind of problems could come up from having multiple devices on a single channel. for example, its a production line and has 30 stations, what problems could come up if Im managing all the devices on that line using one channel in the Kepware OPC server. If one fails to communicate does it move on to the next one or does it stop. Things of this nature is what I'm hoping to trouble shoot before I move forward.
The only problem I can think of is slower communications. As a matter of fact, KEPWare does recommend splitting multiple devices into several channels. If one device in a channel is down, it should not affect communications with others.
I ususally keep no more than 5-6 devices in one channel. It has to be noted though that I don't do contunuous communications - only on-demand reads and writes.
Some OPC Servers support an advanced polling engine that will poll all devices and exclude the disconnected devices from the polling cycle. Once the disconnected device goes back online, it gets added back to the polling cycle. This will prevents any delays when any device goes down. Also those advanced engines supports round-robin polling so it ensure that the your network bandwidth is not bogged down and that you will receive all data in real-time and at a fast update rate. MatrikonOPC Servers have this Advanced Polling Engine. We call it SCADA Framework. Take a look at the SCADA Suite here.
Hope this is helpful
Wassim Daoud
Global Solutions Architect
If comms fails on one device, it will take longer to poll the other devices. It gets stuck on the failed device (I think doing retries). There are probably settings that will help, but I usually put only one device per channel.
Hi, In a project I have four Progressive Pressing Machine. Each machine with different PLC like Mitsubishi 'Q00UCPU' with...
3,059
Dear all, It's my first time configuring the cimplicity taking values from a remote Kepware OPC server on a Windows Server 2012 station. I have...
4,830
I connected s7 300 plc to pc via siemens mpi usb adapter.I used simentic manager and view the data.It is working with simetic manager.But i can...
3,037
Hi, I have an energy Conzerv EM6400 meter giving data on RS485 modbus and Kepware OPC server taking data via MOXA RS485 to Ethernet converter. Now...
7,429
Thanks for this valued information I’m using converter form usb to rs485 and try to connect delta dvb sv plc to opc server kepserver ex and used...
3,415