Hi guys,
I have an issue I cannot solve by myself ...
While commissioning, the E-STOP was pressed and now the servo is in half cycle with MSO showing ERR 22, safety reset did not help and now I'm stuck in the middle of cycle with it.
Does anybody have any idea how to move on, please?
Thanks for any answer!
The MSO command can get stuck if it gets interrupted before finishing. You have to manually clear it's Enable to get it to reset properly if this happens.
Error 22 is "Attempted to execute on an axis while the axis was in motion" which would seem might be caused by the ServoActStatus or DriveEnableStatus on the Axis being true when it shouldn't be.
Try sending an MSF manually from Motion Direct Commands and see if that clears it.
I have started adding MSF before MSO commands in the logic to stop this from happening as I have seen it on occasion, and it really isn't clear what is happening when it does.
Hi, Just after some help with the following issue we are having. On the Kinetix 5500, if the servo is in motion and the MSF is executed, what...
4,729
Hi everybody, What are the suggested status bits of servo axes before starting MSO that will ensure a MSO activation without ER. My current...
4,614
Hi, Have Kinetix 5500 on 5069-L310ERM controller. Why DC Bus is not shown in controller tags. I mean the value of the DC Bus. On the Kinetix...
28
Hi all, I am upgrading a couple of 2094-BC01-M01 servos with 2198-H015-ERS. The original code uses MSG instructions to control (release, engage...
92
Hello everybody, I have Kinetix 5500 (2198-H040-ERS). I'm having issue with this drive. (I believe it's the drive/Kinetix and need confirmation)...
74