Just set up communications to a controllogix processor and now all my PLC 5 and 500 tags are not working any help would be appriciated.
Hi
Maybe you could expand a little. Is it a panel view and not a panel view plus.
Could you let us know what way are you connecting to the l553. If its a l553 why have you plc 5 tags. Is it new or are you jst adding some items.
Donnchadh
An L553 would be a 1747-L553 ( SLC5/05).
Have you just changed to a Controllogix processor?
Please provide the complete catalog number of your PanelView.
Yes it is a half a mile away I just checked it i have a type error on a contrologix tag My legacy tags are working
The Actual Issue was......
In my ControlLogix processor I had one tag B3[0].4 configured as an INT this tag must be a DINT in the ControlLogix What was wierd is that that one tag made the whole screen look like it was not working untill the tag was properly formatted in the ControlLogix ...."Just passing this on if someone has the same problem "
Thanks Guys for the help
Murph
Similar Topics
Hello, I have a system that use to have a 1747-L542C 5/04 CPU -32K Mem. OS401 Series C FRN 3-8 and was upgraded to a 1747-L553 5/05 CPU - 64K...
Replies
1
Views
1,605
I am having problems establishing comms with a SLC processor (5/05 32K) to set it up for a new application (it was removed from a machine and...
Replies
4
Views
2,456
I have a mer or apa file for Pv1000 (2711p-rdt10c) and i need convert this files for Pv5000 (2715P-T15CD-K). Are exist a conversion tool for this...
Replies
1
Views
865
Hi, im looking to migrate a 2711-K10C10 to a 2711P-T12W21 Panelview Plus 7 Standard. I migrate the PV1000 application .pba file in FactoryTalk...
Replies
13
Views
1,986
Hi there everyone! Long time lurker, first time poster. I am doing an SLC-5/03 to CompactLogix migration and am having an issue with a barcode...
Replies
1
Views
1,056
Back
Top Bottom