Thanks again guys !!!
Unfortunalely for me I won´t be able to deal with this problem for the next two or three weeks because it was needed to run the actual automation system so that a test can be done in the hyperbaric chamber. That´s why I can´t verify the feedback you gave me before answering this post, 93lt1, and following your sugestion Rube.
I´ll answer the questions posted by you 93lt1 and, when I can test the program in the PLC I´ll post a new message here.
"Are you saying that when you toggle N7:18/1, B3/320 comes on, and in rung 53 turns on O:18/4? Does O:18/4 turn on in RSLogix?"
That´s the problem. When N7:18/1 is toggled and B3/320 is turned true, O:18/4 is not turned on, although I:14/2, I:13/5 and O:18/5 allow rung continuity.
"You are running the logic in a SLC aren't you? Is the SLC in Run mode (or REMRUN)?"
Yes, the SLC is in Run mode.
"Is the Pump motor starter wired to the correct output?"
Yes, it is. I´m only designing a new automation system which will use the same inputs and outputs of the old one. All the inputs and outputs of the system were already wired.
Thanks a lot !!!
Unfortunalely for me I won´t be able to deal with this problem for the next two or three weeks because it was needed to run the actual automation system so that a test can be done in the hyperbaric chamber. That´s why I can´t verify the feedback you gave me before answering this post, 93lt1, and following your sugestion Rube.
I´ll answer the questions posted by you 93lt1 and, when I can test the program in the PLC I´ll post a new message here.
"Are you saying that when you toggle N7:18/1, B3/320 comes on, and in rung 53 turns on O:18/4? Does O:18/4 turn on in RSLogix?"
That´s the problem. When N7:18/1 is toggled and B3/320 is turned true, O:18/4 is not turned on, although I:14/2, I:13/5 and O:18/5 allow rung continuity.
"You are running the logic in a SLC aren't you? Is the SLC in Run mode (or REMRUN)?"
Yes, the SLC is in Run mode.
"Is the Pump motor starter wired to the correct output?"
Yes, it is. I´m only designing a new automation system which will use the same inputs and outputs of the old one. All the inputs and outputs of the system were already wired.
Thanks a lot !!!