Length of wiring
glpdrumerx
Oct 2006
Tennessee
48
I have a project in which we are extending a furnance 100 feet. It is appox. 120 feet from the control panel to the end of the line now. We plan to add a panel with terminal strips at the junction point and rewire from there. Should I be worried about a drop in voltage for motors and control wiring at the new distance? With conduit drops the estimated total distance should be 250-260 feet.
Will you motors be on drives? Definitely check the drives recommendations as far as output line reactors at that distance.
There are a number of online voltage drop calculators, but in general a motor isn't going to care about the voltage drop in a 250' line that is properly sized for the motor.
Instrumentation might be a different issue. 4-20mA instruments should be fine. Thermocouples might need a transmitter, emphasis on might, because T/Cs often work just fine at that distance, but not always. If you have any TCs then try it out ahead of time and then be ready with a contingency plan.
What about 120 VAC I/O? At what distance would these be a problem?
If the distance is under a 1000' I am pretty sure your 120 dicreet I/O will be ok. I have ran discrete I/O over 2000' with no issues.
Disclaimer... This is using a 16 AWG wire
Hello everybody, I believe that I will find experts here who have already solved a similar topic. I need to calculate the length of the...
367
Maybe this is just not possible, or maybe I am doing something wrong. Background; I have a data array of over 1500 products. For sorting I...
778
Hello all, I see that the Block Transfer Read instruction can read a max length of 64 words I have a Hilscher gateway to map DeviceNet Slave to...
854
Hello everyone, I'm working with an old ACM3710 device and I'm encountering an issue with the data frames I'm sending over an RS232 connection...
694
Good day all. I have an RS-485 topology question. I am hoping for some guidance so that I can make a confident calculation/decision that this will...
1,539