I am working on a design of pumping station consisting of three (3) pumps two duty and one standby.
I was wondering what is better to detect no flow against a closed valve, is it limit switch on the check valve downstream of each pump or flow switch on each pump discharge?
If I chose proximity switch I feel on the long run it is better since it doesn't have any moving parts like the flow switch or a mechanical limit switch
all it needs is periodical maintenance to clean it.
I really appreciate any thought on this
regards,
charbel
dear,
regards,
charbel
You can get flow switches with no moving parts.
I'd have thought both were necessary (in fact I'd go for open and closed switched for the valve) but as ever it depends what sort of budget you're on.
In the stations I've built and or serviced...Generally, since the pump control valve was part of the control system, a limit switch on that was integral and a flow switch as well protects against no flow conditions for any number of reasons. budget not withstanding
For me it would depend on the severity of failure. If it's basically just used as a status bit and you're just going to use it for data and basic indication I'd use a limitswitch. If it's a higher impact and important to your process I'd put both so you can put alarms in place.
You don't mention whether you are pumping clean water or sewage. It matters.
I generally try to avoid anything inserted into the flow stream for sewage - it will attract rags and other debris, causing a switch failure at best and plugging the line at worst. In that case a limit switch on the check valve arm is better. Bear in mind that at low flows the check valve won't open completely unless the sizing is done right.
For potable water either will work. I'd avoid the paddle type flow switches as they are prone to mechanical failure. There are thermal type flow switches that seem to do well and only insert minimally into the line.
Dear,
thank you for your feedback, they are very helpful.
What about using pressure switch downstream of each pump to detect against a closed valve?
That will work, but you have to pick a pressure setting that is above the maximum system pressure plus local valve and fitting losses, yet is within the pressure capability of the pump at minimum flow.
Thanks, do you think it is reliable to be used as hardwired interlocked. When blockage is detected downstream of each pump, the pumps will stop
Yes, it will be reliable. The high pressure setpoint should be at around the shutoff head of the pump(s). If this is a sewage application consider using an isolation diaphragm to minimize clogging of the switch port.
OK. I guess I'm getting old and forgetful. Maybe someone can wake my brain up. I have a TopWorx Limit Switch P/N DXP-E20GNEB that has 2 P&F...
987
For our system using a sureservo drive with Ziplink module, we have a limit switch that will be our "Home Sensor." Should the limit switch be...
1,078
Hello all, I am working on a project involving some stepper motors and limit switches. I am utilizing an s7-1200 1212C DC/DC/Relay. I have a...
2,973
It's off a pallet positioner that doesn't have a name or model number. The body is all plastic. I epoxied it back together but that probably won't...
4,395
Hello PLCS hombres! I have a question according to input status message with CAN. So i want to send a limit switch input status through CAN. I...
1,242