TopWorx limit switch and PLC

muusic_man

Member
Join Date
Nov 2008
Location
Delaware
Posts
148
OK. I guess I'm getting old and forgetful. Maybe someone can wake my brain up.
I have a TopWorx Limit Switch P/N DXP-E20GNEB that has 2 P&F NJ2-V3-N prox switches in it for open/closed position. My SLC has a 1746-IB16 - 16 Input 24VDC Sink Module.
Can someone make my life easy and tell me how to wire these together?
 
I did a quick Google lookup of the part number. The P&F switches you cited are NAMUR devices and need to be wired across an intrinsically safe barrier. They can't be directly wired to the PLC input module.
If the application doesn't require NAMUR rated components the way to make your life easier would be to get a different limit switch.
 
Crisis diverted. Valves will not be installed in a classified area so I spec'ed new TopWorx P/N with mechanical switches. Thanks for the reply.
 

Similar Topics

Working on a site where they are using a DeltaV DCS system. They are using Topworx DVC6200 controllers on their modulating valves. These control...
Replies
1
Views
1,079
Good day: I am wondering if anyone has experience with the Kinetix 5500 S33 Fault. I have 3 drives in a group set as follows: 2198-H025-ERS2...
Replies
3
Views
47
Hello, I have a motor that we are sending a RPM Speed Output from 0-100% to the VFD. However, the Motor HP needs to be limited to 6000 HP and the...
Replies
3
Views
101
Hello, I have a quick question. I have been using scripts to change the color of buttons. The reason, I am usually using multiple hmiruntime.tags...
Replies
1
Views
122
Good evening all! I hope you folks are doing alright today, as I've got a situation that I believe I've come up with a solution to but I wanted to...
Replies
1
Views
457
Back
Top Bottom