Linking panelview and compactlogix without re-exporting runtime

Paul_Pereira

Member
Join Date
Jan 2023
Location
Amsterdam
Posts
51
I am able to hook up my panelview to plc and set them on the same subnet and through the runtime shortcut the two devices. However, in the field I do not want to re-export a runtime for every IP address change. Is there now way to reconnect the PLC and HMI without re-exporting the runtime? I ask because I tried already the following:

1. Using Rslinx to change the PLC ip address
2. Using the View ME station terminal config to edit:

A. The terminal IP address itself through terminal settings
B. Factorytalk linx enterprise commnunications
C. Shortcut of the runtime through the terminal settings.

I reset the terminal and still no luck. Had to re-export a runtime with the shortcut to the PLC.
 
I have never used PanelView, but how does the PanelView application know that the IP address of the PLC has changed?
Can you not program a maintenance screen in which a property page for the person responsible for the machine can write the IP address of the PLC to some variable/tag within the PanelView, and have the shortcuts to the PLC use the values in this variable for the message instructions to the PLC?
 
I have never used PanelView, but how does the PanelView application know that the IP address of the PLC has changed?
Can you not program a maintenance screen in which a property page for the person responsible for the machine can write the IP address of the PLC to some variable/tag within the PanelView, and have the shortcuts to the PLC use the values in this variable for the message instructions to the PLC?
According to Ken this can't be done. I also don't see any global connection with regard to IP.
 

Similar Topics

I would like to cause an HMI tag to change value (digital) when a certain PLC tag changes value. Is there a way to do this? Specifically I would...
Replies
2
Views
1,910
Ok guys i was looking to see if anyone has any insight to what could be my problem: what i have as a working PanelView1200(tested with a loaded...
Replies
4
Views
4,249
I am developing an application for a Panelview 1000 using Panelbuilder32 V3.8. I have an indicator pushbutton and I want to flash the button...
Replies
6
Views
7,298
So I'm currently in the process of linking 2 1756-L72 processors to send alarms back and forth. One processor is rev 26.13 and the other is 32.11...
Replies
2
Views
128
I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
Replies
9
Views
222
Back
Top Bottom