Load Resistors on a Micrologix 1100 & 1746-IF4?
wlr3m4
Oct 2017
Saint Louis
28
I cannot find anything anything in the manual for a load resistor, does this PLC not have any built in? Is it a dipswitch setting?
ML1100 expansion module or embedded analog input?
If expansion module, is it a 1762-IF4? If so see specs below
voltage 200K ohms
current 275 ohms
Embedded analog on a ML1100 is voltage only at 210K ohms
There is a dip switch on the 1762-IF4 to select the type of input current/voltage.
That why 0-10V voltage instead of 4-20mA current is bad for an analog signal.
Always go for 4-20mA.
I have recently received a piece of equipment from an oem with an Allen Bradley Pico controller. I have pulled wires and set it up to run using a...
4,044
Hello, i've been at this for months now, i tried creating accounts on the aveva website but it seems to never approve my accounts or at least when...
74
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
245
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
112
