Lockout/Tagout Program w/ PLC Output

i did use wincc (HMI) create a button and name it as tagout .this button provide with password where only maintenance personal and manager level carried it..once they press the button it shut down the wanted out ( create ladder as N/C) and i fix relay to indicate which panel (stater Been tagout) .after that maintenace personal will do lockout at Panel stater panel and a signal back to PLC as input and massage appear on HMI mention been lockout by maintenance personal.

even when operator accidently click it it wont start the stater board or energize the output.

No way an HMI would work as LOTO in the states. It MUST be a mechanical disconnection of power supply voltage, meaning if you are locking out a motor it must disconnect the power portion of the motor circuit.
 
As Sparkie stated, A LOTO system must have a "Lock" for each person working on the system. That means if there are 4 or 5 working , there must be 4 or 5 locks. Each with there own key and only 1 key controlled by the single person.
JMO
 

Similar Topics

My organization has reached a point where it is now necessary to have a formal Lockout Tagout SOP in place. I have been tasked with writing the...
Replies
5
Views
2,916
Hello everyone, I just sat through our annual LOTO training refresher, and afterward, the engineer in charge asked us for suggestions on ways to...
Replies
9
Views
3,019
I'm hoping someone may have some information. I'm just trying to educate myself because we will have some projects coming up with some customer...
Replies
3
Views
1,437
Hello to all, So while working with a SEL lockout relay I ended up burning the contactor and have not been able to find a replacement. Could...
Replies
1
Views
1,026
Hi all, Just got a request from a place where I recently installed an FTView SE system to add a "clean screen" button. I started asking about...
Replies
15
Views
8,165
Back
Top Bottom