I'm having an issue with a PID loop I am looking at.
It is set up to control a temperature control valve. When not controlling the valve using the loop I place the loop into .SWM mode and give it a .SO of 0 if off, or a value from the SCADA based on what the user wants to control it at.
I've noticed while I'm in .SWM that the integral accumulator jumps to 159. The code is clearing out the setpoint while in SWM so I am guessing the PID loop uses the integral accumulator for some function.
However when I place the loop back into Auto, the accumulator remains at that high value and thus the output jumps to 100% (if it wasn't there already).
Obviously there is an issue in the way I am handling transfer from auto to SWM. I would like to be bumpless. Do I need to use the Tieback? Should there even be anything in the Tieback range in the Scaling tab? I always thought Tieback was only used while in .MO to set the output of the controller.
Thanks
It is set up to control a temperature control valve. When not controlling the valve using the loop I place the loop into .SWM mode and give it a .SO of 0 if off, or a value from the SCADA based on what the user wants to control it at.
I've noticed while I'm in .SWM that the integral accumulator jumps to 159. The code is clearing out the setpoint while in SWM so I am guessing the PID loop uses the integral accumulator for some function.
However when I place the loop back into Auto, the accumulator remains at that high value and thus the output jumps to 100% (if it wasn't there already).
Obviously there is an issue in the way I am handling transfer from auto to SWM. I would like to be bumpless. Do I need to use the Tieback? Should there even be anything in the Tieback range in the Scaling tab? I always thought Tieback was only used while in .MO to set the output of the controller.