ControlLogix 1756-L61 PID Loop
scantime
Apr 2014
US
25
I am in the process of implementing a PID loop for dosing to a water system. I would like to use an analog input for a water quality sensor as the process variable. for the control variable, my only option is a solenoid valve that releases the chemical being sensed into the water, a BOOL value. As the help file states that the control variable needs to be: "SINT, INT, DINT REAL", I'm assuming this is typically some sort of proportional valve, VFD etc. My question is, can I make the control variable a timer value that holds the valve open for shorter/longer periods of time and apply that to my BOOL solenoid valve?
If you can program in FB you can use the SRTP instruction (Split Range Time Proportion). It is commonly used for heat / cool applications.
TIP: You need to watch the min on time to make sure the pulse is long enough for the valve to actuate.
Using pulse width modulation to control the valve is fairly straightforward but I would recommend looking at your application in more depth before you commit yourself to a control strategy. The sort of dosing you suggest usually gives a very non linear response so it is normal to use some form of feed forward driven by flowrate with PID used for "fine tuning" the result. This is a very common application so there should be lots of advice available on the web. If this is for potable water you need to be very sure about what you are doing before you start adding chemicals into it.
hello i had a 1756-l61 with firmware ver 13.24. a solid red made the processor not functioning. i ordered a processor that came with firmware ver...
3,820
1) I am currently trying to integrate a Prosoft MVI56E-MCM Module into a 1756-L61 CONTROLLOGIX5561 that is a redundant system (CPU is redundant...
3,422
Good Afternoon , We have a ControlLogix 5561 controller. The maintenance group , powered down the machine and lost the program. The battery...
5,127
Hi I am new in ControlLogix, so I don't know the details of the scan cycle, I have been checking a couple of programs and I have found the...
1,965
Hey Everyone. I have just installed a new remote rack to an existing controlLogix system. It is rack 6. The last card is an analog input module...
2,485